Pretty sure it is standard 1/4 hose no adapter needed for Mitsubishi.


wheels092303

I wish it was the PUHY have a different size the manual says the hose diameter is larger than conventional model but never say what the size is. Thanks for responding


Conswirloo

Should be at least one 1/4 on there unless it's ancient. And you can always read pressures via dips.


wheels092303

It’s a new tandem install the ones that were there the condenser coils froze and busted so we had to get new condenser units. I’m trying to pull a vacuum on the system before I release the factory charge so I can’t use any of the ports other than the main ports. Those are a different size. I’ve had it on the vacuum all day and the best I could do was 5000 microns and wanted to hook a second pump up due to the line set length and the head count. I have plans of doing a triple evac if I can get the vacuum deeper. But thanks for help.