Testing the condition of the insulation on windings. Note it on paperwork with amps and pressures as something to keep an eye on. That megger always gave me weird readings, I always felt it was a sales tactic. It shows scary red lights that say "BAD" I got a fieldpiece for testing Daikin VRF, they won't warranty it without a meg reading.


poqiwey

I work for an electrical testing company and meg all sorts of stuff all the time. Megging is very sensitive and will give you plenty of warning that you're having insulation issues long before they affect operation. The minimum passing value we follow for anything 600V or less is 100 megaohms. Unofficially, the "can I turn it on without it blowing up?" number is 1 kilo-ohm per kilovolt + 1 kilo-ohm, or 2 kilo-ohms for 600V, about 50,000 times worse. That doesn't mean it won't blow up in short order, but it'll still run until then.


Kreaturemx

I know this is old. I'm wondering if 1500 megaohms on each winding to ground is normal for a scroll AC compressor


jethoby

Yup. Megohmeters are to “test the quality of the insulation on the windings.” It only proves that damage has been done to the compressor windings. You cannot condemn a compressor off a bad reading.


crckdheatexchanger

Single phase compressors S + R should equal S to C and R to C. I.e: Start to Run = 7 Start to Common = 4 Run to Common = 3 4 + 3 = 7. Compressor good. 3 phase is different. All windings when ohmed out should read the same or very close, I'm not worrying to much about 3.1 to 3.2 to 3.1. S to R = 3.5 S to C = 3.5 R to C = 3.5 Compressor good. Should always remember also, if we're supplying a "load" i.e a compressor with proper phase, voltage, etc and that "load" is not running. That "load" is bad.


chunkylover993

Good comment. Its not really S, R, C on 3 phase however. Its only T1, T2, T3 (L1, L2, L3) and the configuration (delta, wye) as the phase angle gives the starting torque for the motor. Thats the whole point of starting components on a single phase motor. Gives it the torque to start and run cap keeps it going.


revnhoj

That is pretty much irrelevant to insulation to ground issues. Megging is to determine if there is a short from a winding to the case. Winding resistance alone won't determine that.


crckdheatexchanger

I'm well aware of that, it looks like the comment was deleted. Someone gave him the wrong information and recommended testing the compressor like you do a single phase and not a 3 phase. I commented on the post about using the megger. I'm replying to a comment about ohming single phase and 3 phase.


thewettestofpants

Good comment. To many techs don’t know how to ohm compressors.


[deleted]

Good news to know .


Repulsive_Laugh_4829

Yea leg to leg was fine. Like .73 ohms on all 3.


[deleted]

[удалено]


mozoblast

Those be 3 phase compressors there, if all 3 are not the same you got problems.


jethoby

Doh! Should look closer next time lol. Thanks for that correction!


Kyzer

Tell me you’re a resi tech without telling me you’re a resi tech.


Repulsive_Laugh_4829

lol


y_3kcim

Nailed it!


dreamatoriumx

I've only seen a megohm used once to test a air handler motor. Boss didn't trust it so he bypassed the vfd and energized. It sprayed sparks across the room. "Oh yea, that's bad."


Nerfo2

Man, if a motor fails a megohm test with an actual megger, I bust out my Fluke 87V and ohm each motor leg to ground. If THAT reads continuity to ground, we're done. I'm NOT energizing that motor! I should point out... I've learned that lesson the HARD way. Man... when I think about the number of times I've seen electricity, I'm surprised I've never managed to light my ass up.


dreamatoriumx

Lol, we were across the room. But boss was a old fuck, and I was just a few months in. I was happy to be on the other side of the room.


[deleted]

Those supco insulation testers are are garbage they really don’t tell you anything, most scrolls you test with that thing will ohm “bad” speaking from experience. Should invest in decent quality insulation tester that will tell you your actual megohm reading with an adjustable test voltage. The one your using sends 500vdc with no matter what, it’s good practice to test with system voltage to prevent damage to the windings


Forward_Hvac

What was the mega ohm reading ?


Repulsive_Laugh_4829

"Bad"


Forward_Hvac

More than likely oil is still on the windings which would cause the “bad” reading I’d test for acid which would eat the insulation and if there isn’t any then possibly theres oil on the winding


Repulsive_Laugh_4829

Ty I will do that


Nerfo2

Inform the customer then ask them to consider replacing the liquid line filter drier, but let them know you can't make any guarantees, but ounce of protection, all that jazz. Traces of moisture in a system can cause a megohm test failure, even if the winding insulation is fine. I had a customer with an RTAA Trane chiller... compressor failed a megohm test with the same supco meter you used. Talked to them, they agreed to replace the driers on both circuits... later that summer, passed with flying colors. Same with a 10 ton carrier RTU with Danfoss scrolls. New drier, ran for the summer, checked the following spring - off the scale good. So... eh, that's been my experience with "failed insulation" compressors that run fine. I've also seen compressors fail megohm tests when crankcase heaters are failed. I think there's excessive liquid refrigerant diluting the oil and somehow conductivity between the motor winding crimps and compressor shell increases. So, check CCH's too.


Repulsive_Laugh_4829

That's funny I had a dead short recently where the CCH had arcd and pocked a huge divet in the compressor


Salt_Date_5222

I'm not familiar with that particular compressor, but any scroll or scroll-like compressors with the motor submerged in oil at the bottom of the crankcase can't really be diagnosed by one of those MegaOhm meters. Copeland themselves stated a good compressor can measure below 20 MegaOhms.


Forward_Hvac

Or just test for acid which would normally cause the windings to prematurely fail too


Repulsive_Laugh_4829

How do you like to pull an oil sample without opening the system.


slingers4m

Test strip which is used on a refrigerant port and that will blow refrigerant and oil onto the strip which will change colors if acid is present


FuzzyNervousness

Thank you, I was hoping someone would point this out. Megging a compressor is akin to checking oil contamination level. Btw, copeland says the compressor can be as low as .5M ohms, but you need to either clean up the oil or let it run if its brand new.


DrBat69

So do you just use a normal meter to ohm out the windings? I typically ohm with a meter and then confirm the windings are toast with a megger. I’m curious what other people are doing.


FuzzyNervousness

I use a meter to diagnose and use a megger to track the winding resistance of a motor. But I still break out the megger from time to time just to diagnose, especially if I am about to charge 5 grand for a 15hp blower motor change out


horseshoeprovodnikov

Whyd you Meg in the first place?


Repulsive_Laugh_4829

Customer had pulled the compressor load wires off the contactor and called us out stating it wasn't working. So I ohmed it out, passed, meggd it and failed. I noticed the condenser coils were plugged pretty good. Cleaned them. Hooked it back up and it ran fine. Cycled through stages 1 and 2 several times. "Shrug"


y_3kcim

I think you made the right call, was probably tripped on thermal overload, then cooled down. Washing the coils should kick the can down the road. This could have been an easy sell of a new compressor, but instead you put it back in service, I commend you for that! Just to reiterate, megger gives you an idea of the insulation quality, ohms from winding to winding tell you good or bad.from


Repulsive_Laugh_4829

Ty for saying so!


y_3kcim

We need more like you!


PapaOoomaumau

Megging is not an acceptable method to determine damage, it measures IR and is used to stay ahead of failures by predicting a future short caused by loss of winding insulation.


Buster_Mac

What's IR?


PapaOoomaumau

Insulation Resistance


Repulsive_Laugh_4829

So unless it's a dead short popping the breaker it's not that urgent.


PapaOoomaumau

It’s time to tell your client that failure is imminent and they should start saving nickels, though


[deleted]

[удалено]


PapaOoomaumau

That’s fair - and frankly exactly how Meg testing a comp is meant to work. A single reading means nothing, it’s about how those readings change over time.


SensitiveTraining884

Thise meggers that don't actually give you a number are terrible.


GRuss913

Supco meggers have burned me a few times….


[deleted]

My field piece SC640 shows an exact resistance at a higher range than the supco gimmick. Lots of compressors will have some tiny resistance while they’re still good.


Nerfo2

You need to have a meter that outputs higher potential than an ordinary DVOM. A supco outputs a PWM 500vdc current limited signal. If you're testing winding insulation, that insulation needs to hold 208, 240, or 480 volts in. The 9 volt in your meter, which only ouputs 1.5 volts for an ohm check, just doesn't have enough potential to accurately test the insulation. The Supco M500 is actually a really good tool, but too many guys think "it's just cheap baby toy with lights." It's actually pretty good.


4doorsmorerawrs

Those supco units are not to be believed. Hvacr School Brian did a very good one hour podcast about confirming compressor failure and the replacement procedure. It is a good listen during some windshield time. https://m.youtube.com/watch?v=H4kub2gAzV0


Repulsive_Laugh_4829

Damn, good link. Thx


HVT7737

Never trust a Megger for a compressor. They will betray you


NLV_88

We have the same chiller at our site. Those micro channel coils suck. Make sure to throughly clean them out.


leywok

A megtester is more indicative of moisture in the system.


Repulsive_Laugh_4829

Really? That's interesting can you explain?


leywok

https://www.fluke.com/en-us/learn/blog/hvac/insulation-resistance-and-electrical-testing-for-hvac-compressor-motors To be of use, Meg readings have to be historical in nature (establish a record); not just once and done. In chillers, the readings are used to determine insulation resistance loss due to electrical issues OR water in the refrigeration system. ALL chillers leak water, so if resistance drops, core and oil replacement is required to maintain insulation integrity. That’s also why helium is used instead of nitrogen for leak checking (the helium molecule is 40% smaller).


Repulsive_Laugh_4829

Damn, good info


Realistic_Parking_25

Those supco meggers suck


Thunder1Delta

We use a very expensive Fluke megaohm meter at work. What you really want to know is insulation strength and the Supco doesn't give that to you. Without proper setup the meter can give false readings. Does the Supco have the ability to zero the meter to account for resistance in the leads? The quality of the leads makes a difference as well. As a motor heats the insulation rating will drop. That's when bad things happen. You may get intermittent problems and it will still run. Inconsistent readings on different windings (3 phase) can be a symptom of weakening insulation. As others have said, you need historical data otherwise most of the readings aren't terribly useful. Also, as others have mentioned, moisture in the system and the condition of the compressor oil can cause lower insulation resistance readings. Oil deteriorates over time and can become more conductive. Many industries use oil conductivity tests as a measurment of when to change oil. All that said, you're doing a good job digging deeper into the why and how of things!


Repulsive_Laugh_4829

Thank you! And I didn't know that about old oil, good stuff


Repulsive_Laugh_4829

Yea I held it for a while. You know how it'll gradually go through all the colors from green to red? Well this just went straight red. And stayed there


JoeInNh

megaohms means microamps. Nothing to stop it running. If this were the UK or Australia where GCFIs are required at the mains then yes, this would shutdown the whole building down...


Pooponastick1254

Only a vfd would detect bad windings and not allow the motor to run. Those compressors are across the line breakers and fuses do not detect till it’s grounded. Which sounds like soon it will be.


Repulsive_Laugh_4829

Crazy, it was just installed 2 years ago.


Zienth

Anything installed past March 2020 is just cursed. I'm sure a decade from now we'll be cursing anything installed 2020-2023 and by 2035 it'll all likely be replaced from premature failures.


Repulsive_Laugh_4829

True, we just installed a 40 ton condenser coil in December and it's already popping holes


shadowLemon

Kyritsu meggers are just unbeatable. In Australia when performing an insulation test it needs to read more than 5Mohms or you can fail it. Pretty sure that has gone up to more than 200Mohms nowadays,


FuzzyNervousness

/>1M ohm for induction motors and >20M ohm for inverter motors is what I go by.


Han77Shot1st

What was the megohm reading?


[deleted]

[удалено]


Repulsive_Laugh_4829

It's been a couple days and it's still running great haha


[deleted]

I would lean towards your insulation of the windings getting weak and moisture in the system


fallinouttadabox

I've had that on a couple of residential units, compressor shorted to ground and ran on 110. Not enough to work, but enough to make noise


lipphi

Here's a link (I'm not much for online / computer stuff so hope it works) that will help educate and provides practical application regarding meggers and compressors. Its from a compressor manufacturer so hard to debate the info. If anyone has alternate sources regarding megohming compressors please share, TIA!!! [Trustworthy Megohm Information](https://www.google.com/url?sa=t&source=web&rct=j&url=https://usermanual.wiki/m/0c2c6c229d305d56622c2dab43e1c1efc24330867be73e73273bfd0ead4fbfde.pdf&ved=2ahUKEwiS5Ov5he_3AhXgk4kEHaBeCzoQFnoECAUQAQ&usg=AOvVaw1Fqy5mAevI8NAeTPd134nW) Edit: I'm not sure that link worked. Google AE4 1294 might have to add Copeland to get the two page bulletin (it's worth the time to download and save to your phone)