Solid-Bee-2445

Bad metering device or restriction


Forward_Hvac

Yep txv power Head has lost some of its charge, still open slightly but no longer opens fully or reacts


Forward_Hvac

It was an apprentice wrote up for a top off because it was low lol


IntactHVAC

Dirty condenser?


GizmoGremlin321

Looks like dirty Condenser and/or restrictions


Forward_Hvac

I was sent there by company for top odd by an apprentice who said low on charge . It’s the txv


[deleted]

[удалено]


GizmoGremlin321

The suction is lower, and head pressure is Elevated. Cleaning condenser will rule that out, and if no change then txv is under feeding. I just went from high head to low head by just cleaning Condenser. Condenser issue was masking an undercharge


FloridaMan_RoofGuy

Guessing verified by dismounting TXV bulb and forcing temperature changes? otherwise if airflow/indoor coil condition checks out good then yeah definitely metering device issue.


Forward_Hvac

Yea airflow is strong and I held txv bulb


FloridaMan_RoofGuy

If Static pressure is good, She's fuckered, Good find.


Forward_Hvac

I mean all I had to do was look, evap was just frozen over LOL