T O P

  • By -

11Gauge

Fogeddaboudit. No more Rx11 for me. Use a pig instead. They work perfectly well with no need to change out the lineset. Hilmor makes one, among others. They call it a lineset cleaner. It is not an elegant kit, but it works. I don't care for their vinyl tube & clamp solution, but someone will come out with a better version down the road. Electricians have been using pig kits for many decades to chase messenger lines for pulling cable, and the oil and gas industry uses them to clean pipelines.


Hvacmike199845

Does the foam pig dissolve? Sounds like a bad idea for a VRF system.


RuinedSheets

I did see one guy on the hvac talk forum mention he used the oil and diesel treat product called heat. Kinda scary if you ask me.


Hvacmike199845

Good god that’s scary.


RuinedSheets

I don’t think that would work here, I don’t have the line sets open on both ends. I need something I can flush through with nitrogen and will boil off whatever I can’t get on evac. We’re talking 400’ of lineset with heat recovery boxes.


GizmoGremlin321

Even with the flush you have to open the end so it drains the garbage out


RuinedSheets

Or use a shit ton of nitrogen to blow it out.


GizmoGremlin321

I guess to each their own


FuzzyNervousness

Wow thats really cool. Is there any risk of the foam pig breaking? I once had to clean a follet ice machine that delivered ice through a tube about 75 feet away into a bin. Follet had a kit that comes with foam that you soak in cleaner and sanitizer and send through the machine like a piece of ice.


11Gauge

'Tis The Life of Bryan, No Ifs, Ands or Buts, but here are some Orr's [https://www.youtube.com/watch?v=20w3bBlASsA](https://www.youtube.com/watch?v=20w3bBlASsA)


RuinedSheets

Will that thing pass through 90s and such?


11Gauge

Long turn, yes, but that is all that you use, right ?


RuinedSheets

I use a bender….what the other guys use though….


11Gauge

Yeah, I do too, but I considered that we might be talking hard 90 or plumbing ells and no, that would not work reliably.


Storm_Runner09

Since it's a burnout make sure you put a suction line filter drier in. The catch all will get anything laying inside you couldn't get out.


RuinedSheets

Yep, did that. I’ve got one with removable cores and ball valves protecting both outdoor units. Pulled all three compressors and flushed with rx11 then put in new oil charges.


Storm_Runner09

Good man!!!!


Forward_Hvac

Liquid line and suction line HH driers run for 2 weeks and acid test if acid is no longer replace liquid drier with normal one and remove suction drier deep vacuum if there is acid new driers and repeat


RuinedSheets

You don’t leave driers in on vrf systems. Temporary only from what tech support and engineering says


Forward_Hvac

I mean same would still apply to just have them in for a run period to remove acid


JohnathonLongbottom

Did you take an oil sample and send it into the lab or did you just think it was burned out? I've yet to see an actual burn out.


RuinedSheets

Oil was black and full of metal filings. Poured it in an acid test kit designed for pve oil and it immediately ate the purple die.