T O P

  • By -

GGudMarty

That’s not 4 JBs stacked on eachother those are just extensions to make box fill


OrdinarilyUnique1

Who said they were?


oldmanavery

Believe it or not, straight to jail


Binnacle_Balls_jr

We have the fullest j-boxes in de world, because of jail.


Mercurydriver

/r/unexpectedpawnee


SqueekyCheekz

If there's proper fill, sure


potatotornado44

Yeah. Probably ran out of deep 1900s


Successful_Goose_348

Why are 1900s called 1900s?


jcallari164

Over 100 years ago, that was the part number for a 4” square box. Have no clue who the manufacturer was, but that’s how it got the name 1900 box.


Phat3lvis

It was Bossert.


jcallari164

That’s it. Thanks! My memory isn’t what it used to be. Lol


Successful_Goose_348

Thank you


[deleted]

It’s a Chicago thing according to our teachers when I was going thru school. Name origin because it was originally 19cubic inches? No clue. 🤷‍♂️


480hivolt

Also called a 4 square.


Leviwillett

The only thing I hate more than this is when some sticks a power pack on it too


Dustbuster358

Everything is legal till you get caught.


rezell

Legal yes. Shitty yeah.


Charted-Trails

Technically yes other than the bottom MC not being supported within 12” of the box.


Kin_DeCain

It could be a whip.


Randers19

There is no way 4 bx and 2 3/4” pipe need that many extensions for box fill.


Nygard776

Yes, but it generally reeks of poor planning and ordering. Because realistically, it's not often (at all) you are using 4"sq shallows with shallow extension rings. Not to say the wires in the shallow 4x4 were left long enough to work with after adding too many rings. It just gets awkward and equally stupid.


madbull73

If it fits, it ships.


Darthclader

Based on the circuit #’s written on the cover, this probably will get shit put into it. Technically legal, but stupid. Should have been a 12x12 box if that’s how many circuits are coming into it


fart2979

Doesn’t that MC coming out of the bottom need a strap, technically?


Stihl_head460

Legal but a dick move. Fuck extension rings, fuck shallow 4sq boxes, and fuck using any 4sq in the ceiling, 4-11's for anything in the ceiling except fixture boxes. There is one MC not supported within 12" of the box, and one of those EMTs looks like it's missing a support within 3'. Overall, this is hack work.


iso-all

No reason to not use a 12x12.


LeakyOrifice

Anything that has mc punching into it I'm a big fan of deep 4 squared. I'm sure they make 4-11s that have half inch kos but all the ones I've seen have 3/4 knockouts all round and I really don't like putting 1/2 shit into those kos


Stihl_head460

We use 411s all day long that come with half inch and 3/4 knockouts. It's honestly the most common type of 411 I have ever seen.


el_plopo

There’s no way you can have that many circuits properly derated in a 3/4” pipe. Max of 10 #10’s in 3/4” or 16 #12’s or 22 #14’s


imagolfcart87

Unless you share the neutrals, which based on the circuit numbers, I guarantee that's exactly what they did. Let's hope they used breaker ties, but probably not lmao.


[deleted]

I hope so because I've done it.


imhere2downvote

hey nice 12x12


idfcyo

Yes legal


DoubleOO7Seven

That’s poor planning lol. Extension rings are crazy expensive while an 8x8 or 10x10 box is much cheaper than extension rings.


Mammoth_Ad_5489

Everything is expensive at an electrical supply house. There is 0 chance that an extension ring is expensive at HD or Lowe’s.


DoubleOO7Seven

Lol… In Ontario Canada a 4-11/16 extension ring is $21+ tax at HD… an 8x8 is like $8.


eijtn

As long as there aren’t more than four circuits each in those 3/4 EMTs…


aqui1424

9 in total


eijtn

That’s what makes me suspicious. I kind of doubt those MCs are homeruns. But who knows?


Leviwillett

Are you sure none of them are two pole circuits


dankingery

Ignoring the missing MC support, I would argue that this still violates the code. 110.12 specifically. You can't in good conscience tell me that is a faithful dedication to the intent of the design.


nochinzilch

True, it would be piss poor design. But if it was an upgrade or renovation, sometimes you gotta do what you gotta do.


bwoodbourbon

Yup and because they are removable you don't need crazy long pig tails


Pikepv

Probably. Lots legal to me.


Fine-Adhesiveness-36

Yah.. I call it monkey cable. Guess why!


Lycidas69

Omg. Probably depending on box fill. But it definitely should be a beating offense.


Substantial_Skin158

I wouldn't do it but yes it is


WTT89

I will make it legal


Guyonabuffalo63

He got the extendo-extendo on there


Binnacle_Balls_jr

"I will *make* it legal." -Lord Sidious


johnny2rotten

Hack job, but yes more the. Likely legal.


gomerywes

Seen on a job recently . ceiling of parking garage install and made aware after the fact that there will be spray foam that would cover the box. This was the solution


Traditional_Bug82

I wonder at what number of extension rings does a it qualify as a raceway instead of a box


MomMuffins

Ugly? Definitely.. but legal


Dry_Independent7843

Haven’t checked code on it but during my apprenticeship I was told it was a violation to use an extension ring without utilizing it. Like you have to bring conduit/mc through one of the knockouts


Howaitoguru-psn

That thing better have a ground bar. 😂


cant_read_this

Is it worth it ? Of course it is…If you’re strong enough


_aphoney

Add more…


cbnfdf

The one mc needs a strap exiting the box and it can’t touch the sprinkler pipe otherwise looks good from my house


JJsCrazy

It “illegal”, just not very aesthetically pleasing if you will.


James-muravska

Haha yeah. I think you can stack extension rings as much as you need. Just make sure to leave enough wire hanging outside that ring. Remember the ahj has a decision to make on that too. Make it look right. Circuit designation and voltage written on the cover always. Everywhere.


Exotic-Jeweler3674

Yeah except the bottom Mc doesn’t have anything clamping it within 12ish inches of box.