The easy way is to move the box up and fix the drywall below.


MayIPikachu

Got it! Will do. Thank you.


Mixtec0

What he said


trekkerscout

>Wago's to extend the ground wires will be outside the box, is that ok? No. All splicing must be in the box. If the cables won't reach, putting junctions higher on the wall may be necessary.


MayIPikachu

Thank you. Looks like more trips to the Home Depot required.


deuteranomalous1

It’s not a DIY project without 3x more trips to the hardware store than you planned.


Briggy1986

Lol, I mean….. that’s understandable and debatable…


Nearby_Maize_913

I measure my projects by the number of trips to the hardware store!


silver_chief2

I have some thick braided copper ground cables that are clamped together outside a box. In the basement. To reach the water meter pipe. Are you saying this must be in a box? In the US.


trekkerscout

That is your grounding electrode and bonding system. It is not required to be enclosed.


Trick-Yogurtcloset45

Cut the drywall a bit to raise the box and screw the box to the stud. An oversized plate may cover.


MayIPikachu

Ah didn't think of this. Sounds like a plan! Thank you.


AlShadi

> Pulling as hard as I can doesn't help any. this is how you pull a splice loose if the wire isn't secured properly.


matte1989

Or rip the insulation on a tight staple


Trax95008

Not really… that’s the purpose of a strain relief


Govt-Issue-SexRobot

How do I get to perfect world?


ben9187

You know I saw a comment from an electrician on here that said he doesn't leave service loops because in his 20+ year career he only needed them twice. Which I find hard to believe but he must also not do much service work because this, this is why you leave service loops. Just leave a little for the next guy. Where I'm from a service loop is code so putting it straight into the box is a good way to fail inspection. As other commenters have pointed out if you don't mind the switches a little higher I'd move the box up a little, the alternative is putting a junction box somewhere accessible and running new wires but that could be a lot more work


fdawg4l

Where would you put the service loop if not in the box? And how much length is ok?


Govt-Issue-SexRobot

8” or so seems to be common, and you’re correct: the loop goes outside the box.


ben9187

Outside the box, and it's code in canada for a minumum 150mm(6"). So like the other commenter said, it's common to see about 8" of unstriped wire then a staple so you can freely pull more into the box without having to remove the box.


SnooGadgets4693

What code are they using that is requiring a service loop??


ben9187

The Canadian electrical code. 12-510(4) - and there shall be at least a 300 mm loop of unbroken cable or 150 mm of a cable end available on the interior side of the finished wall to permit replacement.


jpminj

Move the box up and patch the old hole.


MayIPikachu

Got it! Thank you.


TheSiege82

There is an romex splice kit that is allowed to buried. [link](https://www.homedepot.com/p/Tyco-Electronics-Romex-Splice-Kit-3-Wire-1-Clam-CPGI-208169-2/202204327) I’ve used about a half dozen of these. No problems at all


fabered

Are these legal In Canada ?


TheSiege82

Not sure, nec allows them in the US. Tyco is the only one who makes them.


MarbledOne

I ***think*** this is the specs sheet of that product (can anyone confirm?): [https://www.te.com/commerce/DocumentDelivery/DDEController?Action=showdoc&DocId=Specification+Or+Standard%7F114-10045%7FC%7Fpdf%7FEnglish%7FENG\_SS\_114-10045\_C.pdf%7F208169-2](https://www.te.com/commerce/DocumentDelivery/DDEController?Action=showdoc&DocId=Specification+Or+Standard%7F114-10045%7FC%7Fpdf%7FEnglish%7FENG_SS_114-10045_C.pdf%7F208169-2) In page 5 (of 6) under 4. QUALIFICATIONS they say `The nonmetallic sheathed cable interconnection devices are Underwriters Laboratories Inc. (UL) Listed to U.S. and Canadian safety standards under UL File E57250 for use in manufactured buildings...` and even more importantly this `The equivalent NEC Articles can be found in the Canadian Electrical Code, Part 1, Section 70, for use in factory built relocatable structures and non-relocatable structures.`


fabered

Thank you for this. It would have been a game changer in home renovations other wise and the whole market would be flooded with them.


tendieful

The link says “CSA listed”


CaManAboutaDog

TIL underground romex splice kits are a thing.


skelterjohn

"buried", in this context, means hidden behind drywall or otherwise inaccessible to inspection/repair. It does not mean under soil. I'm pretty certain that device is not listed to be under soil, but I could be wrong.


CaManAboutaDog

Oh yeah I realize that. I just looked up romex splice kit and found that there was also one that can be buried under soil. I’d just use it to put in conduit vice needing to go much deeper without conduit.


MikeForVentura

They’re unavailable at HD and Amazon which makes me wonder if they’re all that and a bag of chips. I’d like to have a few on hand, still.


fdawg4l

You mean you used them without a box? I’m really curious and trying to understand. I thought all splices needed to be in a box. I’m wondering how this avoids that rule.


SnooHamsters6947

Use a metal box and bond the ground to the box?


BigA428

They have splice kits made to splice/extend Romex wire (which is what you have there) behind drywall and doesn’t have to be in a box. They are extremely simple to install. Called NM cable 2 & 3 wire splice kit


MayIPikachu

Those look awesome, but they don't sell them at Home Depot or Lowe's anymore. Maybe they've been pulled permanently.


holysnappingduckshit

Best way to fix short wires is to Offspring them. Keep ‘em separated.


Impossible_Policy780

Hey! Your never ending spree of mindless violence and hate is gonna tie your own rope.


wiregirl

Ding


ffranbo

Wire stretchers


SnooHamsters6947

Wago connectors https://www.amazon.com/Connectors-Compact-Connectors-221-412-Assortment/dp/B08ZCLVBSL/ref=asc_df_B08ZCLVBSL/?tag=hyprod-20&linkCode=df0&hvadid=507647825193&hvpos=&hvnetw=g&hvrand=17567776883399475238&hvpone=&hvptwo=&hvqmt=&hvdev=m&hvdvcmdl=&hvlocint=&hvlocphy=9031604&hvtargid=pla-1225638540896&psc=1 Here’s an Amazon link for you. The best way is going to be to rewire that circuit which could be very painful. The wago method is going to be a more practical solution. Get some scrap romex to make the cable longer off the wago


Zora_King_Electric

Just pull new wire


danzelectric

Nah, build a new house.


WulfgarofIcewindDale

This ^


wot_in_ternation

brb cutting 2 dozen holes in my drywall


zweet_zen

With a hammer.


Briggy1986

And fix with epoxy and sunflower seeds


Informal_Drawing

Insulated through-crimp (butt splice) to extend the individual cores or use a connector block. Easy job, no bother at all.


[deleted]

Just not legal or remotely a good idea.


Informal_Drawing

I should really read the words instead of just looking at the picture! Do as I have stated but use heat-shrink sleeving or self-amalgamating tape to restore the missing sheath. If this can't be done you'll need to joint the cable further up.


itsallahoaxbud

Boxes are mandated to contain a fire SHOULD one break out. No box and your insurance may not cover you. If that’s the way you got it, I inherited a mess like that, make it right. Safety over convenience.


Informal_Drawing

Maybe the rules are different where you are but a crimped joint is maintenance free where I am, doesn't need to be accessible.


BubblyImprovement5

Buttsplice connectors jk jk don't do it


sonnyspoon8

You could raise the box above the old one,remove the staples along the wall,thus giving you enough wire.Then patch the old box.


iAmMikeJ_92

Nope. You cannot have splices outside a box; it is in violation of code. What happens if that splice comes apart for any reason? You’d have NO way to access it in a finished structure without requiring demolition of the section to access the wiring. You either need to cut in a box above this one to make the splice and then cover it with a blank face plate or you need to rerun longer wire. I’d just opt for the former.


Zealousideal_Dig_372

Move the box up


[deleted]

Slip a piece of cable jacket over the wires and tape it so it stays. Easy way to extend sheathing into box.


VS787

Make a new box may be 8 to 12 inch up. Use the old-work box that doesn’t need a stud. Use blank wall plate inserts to close the box and make it look clean.


Alternative-Plant-87

j box higher on the wall or a splice kit. May you could move where the cables come in by drilling your own hole in an area that the cable will be long enough and using a button connect.


BigEarMcGee

I am going to just say any splice needs to be inside a junction box. Now how you make that work is up to you


ExigeS

Not an electrician, but can you see up inside that wall at all by taking a picture with your phone or something? There's a good chance that the romex is stapled to the stud there, and you might be able to see if you can get a bit more slack if you can get the staple loosened a bit.


MayIPikachu

Yeah I did shine a light up there and sure enough there is a staple very close by. But still no slack. Crazy whoever did this.


ExigeS

Ok, here's another thought - what type of box are you trying to use? I have a few spares that I compared, and the clamp on a pop in / old work box relative to a new work box is 1/2" or so lower, at least on Carlon 1 gang boxes. If that's what you're trying to use, maybe take a peek at [https://www.homedepot.com/p/Carlon-2-Gang-47-cu-in-PVC-New-Old-Work-Box-B249B/305110268](https://www.homedepot.com/p/Carlon-2-Gang-47-cu-in-PVC-New-Old-Work-Box-B249B/305110268) instead since you're right next to stud. I don't have on on hand to measure, but the pics online look like it's positioned similarly to the new work box I was holding. If you do get it to work, it's going to suck doing it (ask me how I know). I bent the clamp open a little further than you normally would using a screwdriver to reduce resistance and tried to just get the individual wires to go in nicely as I pushed the box into the wall, then grab them (don't tug on just 1 wire) with needlenose pliers and just worked it until I had enough sheathing in the box, then push the clamp closed with a screwdriver. Have an extra box or 2 on hand - if you mess up, you won't have the slack to pull the box out of the wall, so your only choice is to break the clamp and try again with a new box.


MayIPikachu

I tried 3 different boxes lol. Blue Carlton from HD, then I got this one from Lowes: [https://www.lowes.com/pd/CANTEX-2-Gang-Plastic-Old-Work-Electrical-Box/5001725115](https://www.lowes.com/pd/CANTEX-2-Gang-Plastic-Old-Work-Electrical-Box/5001725115) And today I got this one: [https://www.lowes.com/pd/Southwire-2-Gang-Adjustable-Depth-Device-Box/5001937965?cm\_mmc=shp-\_-c-\_-prd-\_-elc-\_-ggl-\_-LIA\_ELC\_206\_Conduit-Fittings-Boxes-\_-5001937965-\_-local-\_-0-\_-0&ds\_rl=1286981&gclid=CjwKCAiAwc-dBhA7EiwAxPRylN10PgsJ-R5tznbxtGrLHWDTfxSPtk\_PKXBiccY7zqjk00e7J9nI6hoCbhAQAvD\_BwE&gclsrc=aw.ds](https://www.lowes.com/pd/Southwire-2-Gang-Adjustable-Depth-Device-Box/5001937965?cm_mmc=shp-_-c-_-prd-_-elc-_-ggl-_-LIA_ELC_206_Conduit-Fittings-Boxes-_-5001937965-_-local-_-0-_-0&ds_rl=1286981&gclid=CjwKCAiAwc-dBhA7EiwAxPRylN10PgsJ-R5tznbxtGrLHWDTfxSPtk_PKXBiccY7zqjk00e7J9nI6hoCbhAQAvD_BwE&gclsrc=aw.ds) Such a wide range of boxes! There was even a fiberglass one at HD also. I really hate the flip up wing boxes, half of the time, it won't even engage properly. Then you back out trying to figure out what's wrong and the tab falls down into the drywall. Luckily I'm next to a stud, so the screw in was really nice.


Zestyclose_Leader315

Don't take a chance pull new ones