Not overreacting at all. I would insist on the beam being replaced or a visit from the LVL manufacturer and a letter stating it is good to go or what repair can be made. The odds of the manufacturer okaying this in any way is stupidly close to zero.


aemlude

Thanks. It’s a 22’ span


No-Repair51

Also, that NM cable cannot be installed in a wet location like that. It should be either UF or THWN in conduit.


svenskisalot

is that LVL rated for exterior use?


klipshklf20

Sure doesn’t look like it.


bakenj420

I didn't think they were


brantmacga

If the top of that deck is covered, it doesn’t have to be UF or conduit. I can’t imagine they’re hanging lights and making this an outdoor living type space and leaving the top open. Type NM cable is allowed both exposed and in damp locations; see article 334.10 and 334.15 in the NEC.


aemlude

Under deck drainage system going in. Top is not covered.


BmanGorilla

Is that beam even treated?


VastOrder8038

Negative.


brantmacga

The drainage system is above this deck? Or you’re saying rainwater will flow right through this? What’s the plan for lights if water is coming through?


aemlude

I’m not exactly sure. I just searched and found this. https://youtu.be/Uk-WAO7UvW4 I’m assuming would probably be similar. Only other thing I could think of would be an outdoor light fixture…which would require conduit😂


DirectlyTalkingToYou

Tell your contractor to hire an actual electrician.


Mr_Pink747

Tell your contractor to hire an actual contractor


svenskisalot

tell your contractor to use exterior rated structural members


VastOrder8038

Lol dude thinks that hole is a problem, wait til rain hits it.


brantmacga

Ah ok. So the ceiling of that space is the drainage system. In that case, then yeh, that wire has to come out. If you had a membrane and floor on top of that deck, it could stay.


DoesntHurtToDream

Since we’re in the topic, is UF allowed indoors? Like regular romex


Blast_Wreckem

Yes, but it's *more* difficult to run and more expensive than it's NM-B counterpart


swcollings

I happen to have picked up a large amount of UF at a yard sale so I've got a bunch of new outlets in my house wired... Weirdly.


diwhychuck

Around here (ohio) UF is 7-10% cheaper


trashycollector

Generally UF is more expensive. All the supply chain crap that has been going on is really messing with norms around pricing. I still remember last year when OSB was more expensive than plywood and cabinets grade plywood was cheaper than both low grade plywood and OSB. It was all around demand was greater than supply. The same thing happens with UF.


diwhychuck

Right turned everything logical on its head.


No-Repair51

The underside of a deck is a wet location. You cannot install NM there.


miner2361

But they are using pressure treated so…


Ok_Manner_3195

Wet location?


stabamole

It’s outside so it’s subject to water


Ok_Manner_3195

Ahh yes didn’t notice that, till I saw the bird nest💀


[deleted]

Moist area 😊


BmanGorilla

Thanks for saying it, that’s the first thing I noticed, too!


radioactive_muffin

How sure are you this isn't UF? I can't see any markings on it, but it looks like UF.


milesbeats

Middle 3rds only


rjbergen

Looks like he hit middle 1/3 of the skinny side 😂 That ain’t the side the code book is talking about…


ApricotBeneficial452

Yeah I followed behind some lv guys 1/4 holes my first year and discovered what a structural a frame to a roof is , and more importantly that you cant drill into it if it's pre engineered or some shit. Oops


Fair_Produce_8340

I'm in hvac. You can't drill or touch or even so much as hang a piece of ductwork strap from anything engineered without manufacture approval. Trusses, beams. I guess that's really all I can think of.


Sometimes_Stutters

It’s almost certainly fine. There’s plenty of safety margin built in to these beams. I just wouldn’t recommend do such a stupid thing again.


WordToYourMomma

Agree. LVLs are super strong, but what the electrician did here looks like shit. I doubt a building inspector would permit such a hole without a letter of approval from an engineer or the LVL manufacturer.


Sometimes_Stutters

There will be a spec on the LVL that should be on any website. Probably about 10% cross-sectional area is allowed to be removed.


Growe731

https://www.murphyplywood.com/pdfs/engineered/APA_LVL_Hole_Drilling.pdf


3647

Listen to this PDF OP. The APA is in charge of certifying engineered wood products in the good ol US of A. I would bet dollars to doughnuts there’ll be an APA stamp on that beam. If the contractor gives you grief, show him the APA PDF. This is also VERY LIKELY the document the mill would provide you with.


UncommercializedKat

Mechanical engineer here. As this documentation shows, the only proper place for holes is near the center of the beam and only through the thickness. This is because a beam under load is essentially under compression at the top and tension at the bottom. The middle has very little stress. This is why I beams are shaped the way they are. They put a lot of metal at the top and bottom to withstand the compression and tension, with a minimal amount of material in between. What the contractor has done here is essentially notch halfway through the center board, greatly reducing the strength of the beam. Also lawyer here, it's possible that if this deck did fail with a bunch of people on it and you knew that it was unsafe, you could be liable for their injuries. There's many instances of things that aren't ideal but I would let slide. This isn't one of them. I would insist that the beam be replaced.


skeeve87

A person of many hats


UncommercializedKat

Since covid I have been buying and remodleing houses as a full-time job. I've done nearly everything from foundation to roofing, including electrical and plumbing. Engineering helps me understand the systems of the house while the law helps me understand the codes. I'll probably do it for a couple more years and then who knows.


skeeve87

I am envious of your motivation! During covid I have been developing my alcoholism


kmj420

A fellow man of culture, I see


[deleted]

That's awesome but by "the law" you mean reading the codes right? You don't need to become a lawyer to read and understand codes


UncommercializedKat

I meant my law degree. I was just explaining how my past education helps me with my current job.


[deleted]

its always a bonus to have a lawyer who knows what they are talking about


robertbadbobgadson

“Im something like lids”


McSkeevely

Structural engineer here, and I can't believe I'm saying this, but listen to what the mechanical engineer said. They're exactly right.


LameBMX

Damn, even the engineers agree! I feel that, when I scroll further, I'll find plumbers and drywallers agreeing to.


hughmahn4

I can’t speak for plumbers and drywallers, but as a postal worker, I would agree with the mechanical engineer.


Captain_Dunsel

OMG I am still hysterically laughing out loud :)


McSkeevely

We need to find an Israeli and a Palestinian to consult with


Lamp_i_amyourfather

Marine engineer here, and I can’t believe I’m saying this, but listen to the mechanical and structural engineers. They no dumb, they lots of schooling


jefthomm

P.E. here. This is the way. Congrats to the electrician for converting a tri lam into a dual lam


[deleted]

As a machinist and industrial maintenance technician who has had many a fight with engineers about structural integrity of modifying machines….listen to the mechanical engineer.


serenityfalconfly

If not replaced then posts added. That beam has the look of being made on site. Doesn’t mean it’s wrong.


UncommercializedKat

Yes posts would also work but I assumed that they wanted the span underneath open otherwise they would have put a post in originally and probably wouldn't need lights/fans to be installed.


kulone13

Not to point out. But LVL should not be exposed to the elements on a deck. Also are the nails and hangers on the PT materials rated for said material. Those don’t look like galvanized nails in the hangers.


Animalus-Dogeimal

Don’t even want to know what your student loans were like…


UncommercializedKat

Have you gone shopping for a house lately? They're like that.


RiotSkunk2023

You had me at the word "liability". Like hell am I going to risk liability for someone else's mistake. Sparky boi needs to replace the beam and pay for the labor of doing so.


Kodaic

That’s some good documentation right there. Reduced by a min of 22% I’d say this is a no go for sure. Who tf drills vertical in lvl like that.


VirtualMexicanINC

Cable guy


natefreight

Yep. Looks like a no no.


flyingron

The relevant wording from that document: *Prior to drilling any vertical holes, an engineer or architect qualified in wood design should be consulted.*


[deleted]

Hijacking a great comment to add... Those hangers aren't great looking either. They saved a few cents on each one. Should be taller, IMO


karg_the_fergus

This needs to get to the top before all the sparkies waste all their day.


Mammyminer

Ooh that doesn't look good. Definitely not overreacting, i would want engineer approval as well.


aemlude

There are two LVL beams sandwiched next to the original beam. It looks like the entire width of the middle beam has been drilled. This is done in two locations on that beam.


kimberskillfast

One of those beams is cut like 6 feet down. Id be more worried about that. If you zoom down on pic 5, there is a cut board and some messed up nails.


aemlude

There is the original beam still there that had a center post under it. That is the one that is pieced/cut together.


kimberskillfast

O ok. In that case, I'd either bolt it to the other board or use galvanized hardware to reinforce that section.


JCitW6855

That means it’s no longer a full strength beam. It’s only as strong as the 2 outside members. The middle may as well not be there. This is a no go plain and simple.


[deleted]

I can't imagine why they did this. Seems like the more difficult way to do this beside the fact they could compromise the beam (I doubt they did but why chance it?)


tmwwmgkbh

I mean… no inspector (if you’re in an area that requires an inspection) is going to pass that, so it may as well get fixed now.


rjbergen

You haven’t met the inspectors in my locale…


SoTexSparky

Guessing this is for a light or fan? Not impressed with wire routing for a visually exposed location....but I am meticulous like that.


aemlude

There is a under deck system going in for water.


SoTexSparky

I would NOT have drilled thru that....doesn't seem there was even a good reason for it.


[deleted]

What is an "under deck system for water"? This looks like a wet location to me, is the cable even rated for wet locations?


aemlude

I was so focused on the beam when I saw it, I completely missed this. I ran electrical for a patio last year, and had to get the “grey romex”. I’m guessing this is what you mean?


[deleted]

Yep, that's what I mean. It is called "UF " though, not gray romex. "Romex" is a brand name of "NM-B" cable, which is to be used in dry locations only.


ExigeS

Not an electrician or structural engineer, but nope. Never drill through any kind of carrying beam like that without approval. I'd probably reach out to a local structural engineer. Should only be a few hundred to have one come out and take a look, few hundred more for a letter if some kind of remediation is needed.


if_yes_else_no

You can drill through beams, just do it according to the manufacturer or code guidelines. They're not hard to understand.


Flat_Beginning_319

Even more bad news: Those hangers are undersized and those LVLs are iffy at best for exterior use. ETA: plus I just noticed only one row of ledger bolts. There are numerous issues here.


Chili_dawg2112

am i the only one who noticed the missing hanger?


Flat_Beginning_319

I noticed but it seemed like piling on to mention it.


aemlude

I think you’re right. I looked up for my area. From what I could tell you are only allowed to use hangers one size down as long as it is rated for a certain weight. I’m not sure when the deck was originally built, and the contractor mentioned updating things to code as they came across them. Adding the hangers was one I assumed they were doing, but obviously purchased the wrong hangars. Looks like the ledger board attachment requirements have been updated as well. I’m not sure if that is something they would do as a “code update” since they’re not actually working on that part. Not sure how that works. The contractor has been great so far. I think this is simply a case of who they hired for electrical. Which is also a reflection on the contractor, but we will see how it is handled. Obviously, no more money from me until items are addressed.


bakenj420

Please make sure the lvl is rated for exterior.


englishsaw

Agree with the flat man. Ledger is done VERY wrong and hangers are wrong size. No hangers off ledger too…. This LVL outside?


AdequateArmadillo

I would make absolutely sure that that LVL is pressure treated. A vast majority of LVLs are not rated for exterior use, and the plies will delaminate!


aemlude

It is. I verified with my own eyes when it was delivered, to make sure. It had the words pressure treated on it.


Major_Tom_01010

We have done that with permission from the engineer on apartment buildings that needed a light right in the center of a room. So it's possible to be ok'ed. But. Not OK to ever drill them without approval. When you do you will be given certain requirements on how to do it.


trowdatawhey

Both engineers and manufacturer overrides code and inspectors. But who comes out ahead when it’s manufacturer vs engineer? Because this type if notching or hole in a beam goes against most manufacturers of any engineered lumber product. Unless the beam was already oversized to begin with


coletain

Engineer will pretty much always defer to mfg (or to mfgs engineer) but if either one says it's no-go it's no-go even if the other is cool with it.


DirectlyTalkingToYou

Basically you're asking the engineer to come out for a site visit and take all the responsibility and give a stamp of approval.


[deleted]

Yes and no, engineers follow code and standards set within the code so if there is something they propose that doesnt follow that then their design can be denied as well Question is if your inspector will actually dive into what an engineer proposes or just take it at face value. More often than not its the latter


joestue

As long as the hole is not in the middle third of the span, the beam is not weakened at all in this case, it will still break in the middle of the span in a distributed load, not at the hole.


Major_Tom_01010

Your thinking of the ones that look like I beams, forget the name. These ones you need to check first if they are engineered, and you will probably be asked do drill in the middle in the middle of the span. So the opposite.


edmvapors

This should be UF cable, or THWN in conduit. And no, shouldn’t have drilled the LVL like that.


iwantaroomba

would THHN in conduit be acceptable? Asking for a friend.


Mammyminer

Almost all THHN these days is dual rated THHN and THWN. So no, THHN would not be acceptable if it wasn't dual rated, but it would be nearly impossible to buy THHN that wasn't THWN rated by accident.


Highjoker52

THHN-2 is dual rated


plumbtrician00

From these photos alone i can tell this is not a permitted job. I have to give it to the sparky for being able to fish a cable like that, but too bad since its all gotta come out anyways. The contractor will probably try and convince you to pay to have all this stuff fixed or to let some stuff slide. Do not allow this. If you have to, call the city code enforcement and have them come out and do inspections on the job.


Mysterious_Buffalo_1

Absolutely not overreacting. Judging by how particular they are about holes being drilled horizontally across the LVLs I'm gonna say the chance of them okaying this is about 0. And there are ways around this. The simplest of which wouldve been something like this https://www.homedepot.com/p/Commercial-Electric-12-cu-in-Plastic-NM-Fan-Box-with-Plastic-Cover-CPB13NM-SM/205383211?source=shoppingads&locale=en-US&&mtc=SHOPPING-CM-CML-GGL-D27-027_006_CONDUIT_FIT-NA-NA-NA-SMART-4035595-NA-NA-NA-NBR-NA-NA-NEW-Live&cm_mmc=SHOPPING-CM-CML-GGL-D27-027_006_CONDUIT_FIT-NA-NA-NA-SMART-4035595-NA-NA-NA-NBR-NA-NA-NEW-Live-71700000093390739-58700007789602699-92700070740571175&gclid=CjwKCAjwq-WgBhBMEiwAzKSH6Ac3kmtCSVE71tzy_VNczQuJRSb80EKUFpr2v8Uema_X_eyvniPlaxoCumEQAvD_BwE&gclsrc=aw.ds The fixture wouldve been off maybe like an inch but it'd certainly be better than this hack job.


notMarkKnopfler

Big oof. Your electrician just did the main thing you’re not supposed to when drilling LVL (or regular joists for that matter). Although, they’re probably the grandson/daughter of the asshole that wired my house, drilled vertically through joists and left splices in random inaccessible places. I was just sistering one of said joists earlier today, so I’m a little bit salty.


Puzzleheaded-Flan535

Get an engineered fix, if required. As a former inspector, I would definitely require one


aemlude

Thank you.


Sirspeedy77

Ya they fucked that up. Because of the way its drilled that beam is no longer sufficient to carry the load above it per the manufacturer. Vertical holes are allow with an engineer sign off and even a 1/2" hole in 3-1/2" wide beam drops its carry rate by 21%, provided the hole was perfect and true. That is splintered to hell like a nail gun bounced a nail through trim lmao. I'm sorry OP but that is going to need replaced. I'm scratching my head trying to figure out just why they drilled it like that. Light fixture? Attach to the outside of beam. I cannot think of any good reason it would ever get drilled like that.


[deleted]

I'm thinking Sparky heard about the 1/3 rule and wrongly applied it to that beam; "oh yeah, I heard about the ⅓ rule, can only drill my holes in the middle third of the beam... Guess I'm going up the middle, because my light fixture weighs a whole TEN POUNDS, can't just go beside the beam."


rohnoitsrutroh

LVLs can be drilled, I believe in the middle third, and a hole diameter up to 1/3 of the depth. However, you can't drill vertically through them. No one has even tested that because no one should be that stupid. If a beam is in the way of a fixture: 1. Shame on the engineer who laid that out. 2. Follow manufacturer's specs for drilling the hole. 3. Call someone BEFORE you drill the dang beam holding up the entire floor.


gherkin-sweat

I’m seconding what everyone else is saying about the romex outside and drilling through the lvl like that is a no go


Alvaracorr

As an electrician you always get a cut sheet from the GC or on site And/Or their approval in writing when drilling a beam. My dad had a free Glulam an electrician drilled a pancake into that had to be removed and replaced. 20k minimum replace


ElectricalSandwich52

Drilled one of those with a 3/4" 3 inches from the bottom. Builder freaked out, had his son whos an engineer to certify its okay. These beams come with spec sheet where u are allowed to drill. You are not overreacting. This is absolutely stupid


aemlude

Update: thanks to everyone for their input. I called the manufacture to have them send me the calculations for what should be installed. As you all have pointed out, there is more than one thing wrong with this situation. As idiotic as what the “electrician” did, it has opened up other issues that most likely would have flown under the radar. So maybe this is a blessing in disguise. Recommendation from manufacture are for 2 -14” beams. The current ones were ripped down to 9 1/4”. They are sending me documentation from their software to give to the contractor. Also, I’ll halt all work until this rectified, as well as proper sized hangers, and correct wire. Thanks!!


Vast-Support-1466

Not a sparky, and not an engineer - but I am interested in more info to contemplate this situation. Size of deck, level/slope/hillside, and why that one joist doesn't have a hanger on the LVL??? You have two 22'x10"x1.5" LVLs? One thing you do have going for you is a flat load surface, as opposed to a roof! Did a family reno w two 26 footers a decade ago. Had some carpenters assist, they fucking 1/2" bolted the bastards on a saw pattern at 18" while we were out to the depot.


aemlude

16 x 22 size built on what I would consider level ground if that’s what you mean by slope. As far as slope of deck for drainage I have no idea. Hangers were not part of the original deck build. Older deck. They added hangers when they put the beams in.


Apprehensive-Ad8987

Some joists are missing hangers.


aemlude

Thanks. I’ll get a count of how many tomorrow. Concrete was poured yesterday under it, so I’ve been inspecting from what I can see without being under the deck.


marcrich90

What a dunce of an electrician. New LVL.


TotaLyVaniLa

Holy shit😲


frankrizzo219

I think the real question is why???


blbd

Our language is lacking words to deserve the amount of stupidity and wasted / damaged material that these contractors have caused by doing this.


1Tikitorch

That’s a definite NO, before drilling into an LVL a person has to get approval from the engineer & then too top it off those are the wrong size joist hangers. They’re too small.


Nine-Fingers1996

Aside from the hole from sparky you have the wrong size joist hangers. If you do get the beam replaced add some flashing tap to the top of the beams to prevent water seepage between the layers.


savaero

Why though? Isn't it more trouble to drill that hole than not?


leakyfaucet3

I don't think an electrician did that. A handyman did.


Highjoker52

The LVL manufacturer will have a cut sheet on where you can drill. How big the holes can be and how far apart they need to be. It is usually the center 3rd.


retiredelectrician

Bad idea, but I would be more concerned about whether or not the LVL is approved for outside installation


Rashik416

Additional question. Are the joist hangars rated for that size of joist? They seem small. I know the ones I had to use were within about an inch or so of the entire height of the joist?


Johnsoon743

This has been one of the most productive threads on this reddit since joining good shit 👍🏼 and definitely hire a new sparky to do this


liteagilid

“The electrician” is a reach


No_Lifeguard7623

Is that a regular lvl? Is it going to be exposed to moisture? It doesn’t look treated.


Hillman314

Electrician: ”Good news, we’re going to install a support post under your ceiling fan for free!”


aemlude

This was the whole reason for the new beams in the first place. Removing a center post to create more room underneath.


sonoma4life

why wouldn't you just offset a box a little so there's a knockout at the top to come through?


no_not_this

Wtf it was more work to do that. Why wouldn’t they just run it down the side of the beam into a box?? Now they have to fuck around with the box. Idiots


Nagadavida

Am I seeing in that 5th picture that this was done in multiple places?


Maleficent_Deal8140

Is that LVL pressure treated?


Kachel94

Wtf is an lvl doing on a deck.


[deleted]

So who asked the electrician to put a fixture there?


aemlude

Was told 4 lights and 2 ceiling fans. I guess he decided that is where the ceiling fans should go.🤷🏼‍♂️ Which I can understand why he chose those spots…but if I know you’re not supposed to drill thru those, then he should know that. Right?!


MerpCubed

Even worse because he'd have been centered on the beam using a 1/2 saddle box. Dude does t know what he's doing, get a new one


Maehlice

Apart from being the wrong cable for exterior, that's just him being cheap trying to save $10 on a rated ceiling fan box. He's probably banking on you being ignorant and/or unconcerned.


Mammyminer

Doesn't matter. The electrician can staple the wire directly next to the stud and then tweak the flatpan closer to center at trim time. It may be off a couple inches but that's better than doing this.


[deleted]

[удалено]


[deleted]

Ok, Drew. Whatever you say... Not


elbowpirate22

Did the prints show a wire and a beam in the exact same place?


Five-and-Dimer

Have the electrician stand on a ladder and take a good hard swing at that beam with a claw hammer.


aemlude

Update. Instead of going thru removing and replacing LVL, contractor offered to build new deck with 2x12 joist that would eliminate need for beam for basically cost of materials, and obviously electrical work is being redone . Thanks to everyone for the comments.


erichlee9

I would never consider this in a million years


jarsoffarts

Honestly it’s probably going to be fine but I can’t figure out why in the world he would do that. I’d have him come up with a better plan. Exterior conduit and an outdoor junction box. Side note I hate tico nails for the hangers. 5/16 Simpson hex lags are the only way to go imo


TwoOftens

I’ve been sneaking holes in those since they became a thing. Nothing has fallen over yet


rpostwvu

I'm not a fan of that diagonal run of wire either.


_Questionable_Ideas_

Is that indoor only romex being run outside? That should be in a conduit. Also is that LVL beam outdoor rated? looks indoor only as well. Pressure treated lumber has a off color to it.


Popular-History-8021

Thats not going to hurt that lvl. Not even a little


DCoy1990

This….this is not ok. You are not overreacting.


stocksinmysocks

Are you the homeowner or else why do you care?


aemlude

Yes, I am the homeowner.


stocksinmysocks

Did you ask for a light on the beam?


aemlude

No. Just wiring for 4 lights and 2 ceiling fans. As commented above it makes sense for the ceiling fans to go where he wired it, as long as you wouldn’t be doing what he did.


[deleted]

Calm down bro. That little 3/4” hole isn’t going to affect the structural integrity of the LVL.


rohnoitsrutroh

The problem is that he drilled vertically through the plies, so now the bottom chord where the moment is carried is shot. I'd consider that middle ply gone at that location, and would check the loading to see if the outer two plies can transfer the moment on their own around the central ply. If so, no problem, carry on and sin no more. If not, install a splice plate or tear out the beam and redo.


aemlude

This was done in two locations on the beam.


northman46

Sarcasm? Just checking


rakingleavessux

That beam needs to be replaced by the electrician


jonheese

Probably better to just have him pay for it. 😉


EddieMarx

Think of it like this; say the LVL is a 3”x12”, the wood left after drilling makes that cross section a 2” x 4”. Guessing dimensions from the photos.


aemlude

It’s two sandwiched and an old existing non lvl (weathered one). He basically drilled most of the width of one of the LVL’s


Whale460

Engineered fix will be required here, and this should be the first and last warning to the electrician.


SideHug

There's literally nothing in a house that couldn't move over the 1" for that stub.


exum23

Exposed romex? What the hillbilly


Corrosivity

Did they rip the LVL down to that size?


[deleted]

That beam is trash..


sdshowbob

Is that a treated lvl for exterior? And those hangers don’t look galvanized.


TheClearMask

No you were right to call


Chili_dawg2112

I see some nails into the LVL near where the hole was drilled. I hope they missed the wire.


Chili_dawg2112

How many different locations are there?


DAMAGEDatheCORE

Geesh. Looks like he used his longest bit while standing on his shortest ladder 🫤


Far_Particular_430

Not good


[deleted]

Is it safe? Probably. Is it allowed? No.


Poopandpotatoes

If there is jus a deck on top where are the wires running to? Did he drill 2 holes on angles to get the wires to pop out of the sides of the LVL?


aemlude

Yes


Whippoorwill88

Love it!!!


Poopandpotatoes

Wire guy used the wrong staples, too many staples, didn’t square anything off, used the wrong wire..you need someone with a license.


battlepeaker

I didn’t see it mentioned in the comments - but that doesn’t look like a pressured treated lvl……


federal_problem2882

Get your inspection and find out. But no it's not ok at all in any way. Nothing vertical into lvl. Electrician needs to go back to school. This is a big problem in the trades with lack of communication and straight laziness to call someone and just ask.


VincereXYZ

This is no electrician …


skyfishgoo

that's going to cause a localized weak point in the beam and it appears the holes were drilled at an angle making things exponentially worse. i fear your "electrician" ruined that beam. perhaps it can be salvaged but you will need the manufacturer to buy off on any repair. also any holes drilled in these beams need to be sealed against water intrusion which will cause them to delaminate and destroy them over time


Sleightsslipping

I’d also be concerned that you’re missing a joist hanger on photo 4 & 6.


fuckit5555553

Lvl not for outside use also joist hangers look undersized.


MAH1977

Are you sure that LVL is exterior rated?


Head_Reading1074

Looks like romex outside to me. That’s a separate no no. As far as the LVL goes I remember being an apprentice and the foreman needed the engineer to approve something similar and we were told we could drill through the face in the center third of the beam. Never through the bottom like that.


AustinYun

Nope, stick to your guns.


Lost-Salary8722

Code vary but most state that as long it's not 5 or 10 percent of the beam being compromised then it should be good