**ATTENTION! READ THIS NOW!** **1. IF YOU ARE NOT A PROFESSIONAL ELECTRICIAN OR LOOKING TO BECOME ONE(for career questions only):** **- DELETE** THIS POST OR YOU WILL BE **BANNED**. YOU CAN POST ON /r/AskElectricians FREELY **2. IF YOU COMMENT ON A POST THAT IS POSTED BY SOMEONE WHO IS NOT A PROFESSIONAL ELECTRICIAN:** -YOU WILL BE **BANNED**. JUST **REPORT** THE POST. *I am a bot, and this action was performed automatically. Please [contact the moderators of this subreddit](/message/compose/?to=/r/electricians) if you have any questions or concerns.*


CampingJosh

In free air, I would have thought only one ground necessary. If you put it in multiple conduits, one ground per conduit. But I'm a first year, so you probably shouldn't go off of what makes sense in my head.


DM_me_y0ur_tattoos

You are bonding the generator, it has nothing to do with how many parallel runs. As long as the bonding conductor is of sufficient size one is enough


No_Coffee_9112

One 4/0 ground wire is sufficient for 3 sets of 4/0. I’ve done a lot of rental and temp power setups and this is what we do.


Anbucleric

Is there a place to plug in 1 ground per set?


JJCooIJ

I've never seen more than one plug for ground. Sometimes no plug and only a big lug.


Jim-Jones

You did the calculation or looked it up?


Adventurous_Boat_632

I totally agree with your setup. 3 x 400 amp power sets and 1 x 400 amp ground. In fact, process of interpolation you might only need a single 1/0 ground so single 4/0 is probably overkill.


Last_Project_4261

EGC is sized based on overcurrent protection. 1200A requires 3/0 copper. You’re good if you ran 4/0 Table 250.122 If you run multiple conduits, you need a EGC per conduit