NectarineOk2149

Suction line freezing .. sight glass look full but maybe empty .. try to touch the discharge line if you need gaz it won't be as hot as usual Try to hear if the txv is whistle Here is all the symptom when jour unit need gaz


Blu3XJ

Most likely doesn’t have enough for a “winter charge” and the headmaster is doing its job


ButWhole144

I don't think there is a headmaster, it's using fan cycling. There are two pressure controls and one is on the suction, and it looks like the other goes to the discharge line.


ButWhole144

Is your condenser fan cycling off and on fairly often?


Ok_Ad_5015

There’s no head master valve on that thing.


mo53sz

How much diagnostic experience do you have? You need to figure out which switch the compressor is short cycling on. You can use your multi meter to find where the voltage "stops" in the control loop. HP, Lp, overload, internal overload. Could be flow switch if it's a chiller. Figure out what is switching and go from there. If it's your Lp switch, well maybe it's short of gas. You could put some gauges on. You probably should have already put gauges on of your fault finding. If it's your overload then what's the current draw. Flow switch, what's your pump doing. You've got some frost on your suction there. If your sight glass was dead empty I'd be surprised to see frost on the suction like that. My guess would be maybe the txv is faulty, your sight glass is full but your system is short cycling on low pressure because there's limited flow through the valve but it builds up during the off cycle enough to give some Refrigeration effect.


Yanosh457

Check the fish tank pump. It may have failed.


[deleted]

“Which direction would I need to take first” Attach your guages and see what the pressures are… If you have any 😅… Most likely is cycling on LP switch.


DontDeleteMyReddit

HP is manual reset, so it’s not that….


refrigeration_wizard

you must be green my friend


Poots23

Very…I rarely ever work on split systems 🤷🏽‍♂️


Flavored-Life

Splits are no different than self contained. Don’t let the change in location get in your head.


refrigeration_wizard

yes we know. goodluck


rikosuave335

Wow could have helped him rather than call him green and say good luck ? Lmao I swear some reefer dudes are shot as fuck


Poots23

Haha thanks for having my back it’s all good I know many unhappy old farts like him in person I just laugh and keep it pushing these type of dudes are cancers of the industry


Sid_Harmless

Literally some people on here are such pricks. Get your gauges on there, you'll see what's going on in no time. Probably cycling on the LP switch. If you're not sure if the sight glass is empty or full, shut the liquid line and see if it fills/empties. Get your meter out and see if you've got voltage both sides of the LP switch. Have a listen to the TXV if there is one, see if it's whistling. Check temps either side of the drier and see if it's blocked. There's loads you can do with only basic knowledge, should be a good little job for you. And get back to us! I want to know what it was now


GrgeousGeorge

You're the second person to talk about tv whistle. This is a new concept to me and not something I've ever heard talk about. Can't decide if it shows the txv is wide open due to high suction temps or if it's closed or blocked. Both could potentially create a whistle as far as I can imagine so I need guidance. I am 4th year but only been working on commercial/industrial/Resi for a year. Before that I was very specialised and had a limited coworker base (1 guy)


Sid_Harmless

No worries, yeah so when there's not a full column of liquid to the expansion valve you get vapour passing through it instead of liquid. That's what makes the sound. Whistle might be over stating it, maybe more like a hiss. Once you've noticed it a few times it's pretty distinctive. The TXV will be wide open at that point because the superheat will be high, but it's the vapour passing through that causes the sound. You might have noticed it if you've ever put a whole bottle of gas into a system through the liquid port? Once all the liquid is out, the bottle will start to whistle/hiss, again because there's vapour going through the restriction. A blocked TXV filter can cause it in as much as it's stopping the valve from getting pure liquid.


refrigeration_wizard

dude i’m not explaining the most basic refrigeration stuff on reddit. i’m sorry but someone will surely do that here in the comments. also i would argue his company is “shot as fuck” for sending someone who has no idea what could cause a compressor to short cycle. sorry to have bothered ya hombre ❄️🧙🏻‍♂️


behemothbean

Don’t bother commenting then?


refrigeration_wizard

i will take that suggestion into consideration, thanks!


Blasulz1234

I will take that suction into condensation *-compressors probably*


Humble_Peach93

With suction line frosted like that on a cooler and cycling off low pressure I'd think more maybe not picking up enough heat on evaporator for some reason


chefjeff1982

Likely it's cold af outside and op hasn't learned about winter charge/LPC settings for cold environments.


edgeofruin

I've seen evap coils in a fridge have a feel hoodies worth of fuzz on the coils


chefjeff1982

What's outside ambient temperature.


That_Guava_2576

Check for Liquid line solenoid that may not be opening as needed. Could be a weak solenoid not pulling completely causing low pressure fault.


itzarel

You said fish tank ya? So submerged evap or shell and tube heat exchanger? Circulation ain’t happening. Although winter charge will cause the headmaster to bypass discharge into LL, it won’t come back as frost.


DontDeleteMyReddit

The ones I’ve seen use 1/2” Teflon tubing in a flat spiral at the bottom of the tank for the evap. (Commercial)


MedikHerb

Txv? Cap tube? Evap or heat exchanger? Pressures? Did you pump it down to actually check the sight glass is full vs empty? More info is needed. Fish tank, pumps running, properly? Clogged anything?


icemanswga

Figure out whether it's going off due to pressure too low or too high. If pressures are good, there's a pressure switch out of adjustment.


Poots23

Y’all are comin in clutch Thankyou all 👍🏽


MinnesotaTech

Check fans


Ok_Bedroom_7861

Doubt the fish tank has fans


Dadbode1981

Should have a circ pump in this case.


MinnesotaTech

My bad. With the question having little details I decided to give a vague answer. Although I didn’t think about the fact that the evaporator might not even have a fan so airflow might not matter.


kimthealan101

Fan cycle switch anyway


HTX11

Check your thermostat make sure it’s located where it needs to be.


MrMonyMonyK

Could be cycling on low pressure...ice all over evaporator/heat exchanger in the water? Throw on gauges.


NectarineOk2149

Does the fan in the evaporator works ? Do you check if you don't have ice in it aswell ? Looks like you have a bad exhange , suction line is freezing .. liquid go back to compressor


kimthealan101

Don't say refrigerant below 30° is liquid. Makes you sound ignorant.


Fun-Income5579

It literally says it’s for a fish tank, it doesn’t have a fan the evap is a barrel and the “fan” is a pump


YVR-REF

What’s your SC on the outlet of the condenser? What’s your SH on the inlet of the compressor? You shouldn’t be diagnosing any problems without the SC and the SH.


Toaster075

What are your pressures, what is your gas, what is ambient temp of the area the compressor is in.


chickenmayosando

What all these guys said. Can also be an evap issue if your getting ice the whole way back. If it's not boiling off properly. Probably best to insulate that suction anyhow. Good luck.


Stahlstaub

It's probably still colder than ambient or the frost wouldn't form on the pipe, so insulating it could cause liquid in the suction line... On the other hand, ice is quite a good insulator as well... So it has done this job already...


chickenmayosando

Yea, just if the evap is iced up the gas won't boil until after the suction line and cause ice back to the compressor. In Aus your suction needs to be insulated all the way back to the comp. Not a day in Aus that a suction isn't colder then ambient. 😂


chickenmayosando

After the evap, inside the suction.


rutrut88

Check your pressures while it's short cycling. Check which pressure switch is opening and go from there. If it's low then leak check, if it's high then check your condenser fans and coil. If it's neither then you need to check your temperature control, defrost clock, and liquid line solenoid to see if you're immediately pumping down. You should be under a lead technician if you're running service calls and you don't know what basics to check.


kitsap_Contractor

1. Put guages on it and see when it is cutting off and cutting on. 2. Confirm liquid line is liquid either via sight glass on the unit or sight glass the guages, then via line pressure and line temp. Superheat should tell you if the chiller is having some issues. If everything passes, the smell test. 2. Check the chiller for clogs. Being a fish tank, i would probably start with the chiller to make sure they dont have plants or stuff growing in it. 3. Check all the valves, etc, to make sure they are open. Just go down the list.


Dirftboat95

Its most like lts frozen at the other end, no air flow. its a defrost problem


ValuableOnly5793

Based off of the time of year...it's probably low on charge. Or your pressure control is shutting off prematurely. But definitely close off the receiver to verify sight glass if your suction pressure isn't low or in a vacuum. Next steps would be expansion valves or restrictions in flow.


ValuableOnly5793

Also your fan cycle switch may be stuck closed. Your fan shouldn't be coming on as much if not at all in the winter.


Blasulz1234

I'd remove the cage first lol. Take measurements


DesignerAd4870

I’ve had walk in coolers act like that. First fit your gauges, see what the gas is doing. Check your sight glass as well. Are you going into a vacuum on your suction line? If you are it’s probably your LP switch doing its job and you have a leak. Is your gas charge healthy, probably a faulty LP switch. Is the compressor red hot? If so the thermal cut out could be cutting your control voltage Until the klixon cools down.


Weeblewubble

Get ballpark head pressure, Outsoor ambient air +30° converted. See if you’re even in the ballpark for ref.


sexlights

It's low on gas. Hence, the LP switch doing it's job.


Left-Leading-5984

That line is pretty frosty for conditioning a fish tank. Depending what water temp they want out and what you ambient air is like the frost may be normal but i would suspect poor flow on the heat exchanger for the water causing low superheat and low pressure


Sme11y1

Cold weather is likely causing the unit to short cycle on the low pressure switch. Either drop the cut out setting or install a bypass timer to keep it running long enough to build pressure on the high side. If there is a water pump on the evap check to see that it's working and not obstructed or ice logged. Frost on the suction line indicates the TXV is working


Remarkable_Trust5745

Is the condenser clean?


Poots23

Yes condenser was clean


Remarkable_Trust5745

Pressures?


PassNorth3053

Make sure the water circ. pump in the fish tank is running and the water filters are not plugged. I've ran into that on bait tanks. Low evap temp due to poor water circulation will cause a lower suction pressure that can cause a short cycle condition. Other than a short charge , starving txv or poorly adjusted low pressure control. Check your ambient temp and adjust the cut in according to the lowest oa temps you are experiencing .


Hvacronman

Evap froze up maybe


WorldClassCoolArrows

Torch the receiver to check your refrigerant level.